OK, in one of my threads I ask about an extension cord for a welder and the thread kinda went all over the place so I think I just start here.
I have a miller XMT 304 CC/CV 230/460V welder. I will be running it in single phase. It says on single phase it will pull 47.4 / 24.5 amps. I want to make a 50' extension cord for it. I had a electrician put in a dedicated 2 pole 60 breaker for this welder.. Im thinking that I need a 6/3 cord, but Iv also read that with the duty cycle and the fact that Ill probably never max out the amps that it would be possible to run a 8/3 cord. Any thoughts?
Thanks
spooky
I have a miller XMT 304 CC/CV 230/460V welder. I will be running it in single phase. It says on single phase it will pull 47.4 / 24.5 amps. I want to make a 50' extension cord for it. I had a electrician put in a dedicated 2 pole 60 breaker for this welder.. Im thinking that I need a 6/3 cord, but Iv also read that with the duty cycle and the fact that Ill probably never max out the amps that it would be possible to run a 8/3 cord. Any thoughts?