Yea, the guy who wrote that is an idiot...
Here's your chart.
View attachment 736316
There's the load info from the bills. The gas bill = the lie detector. Unless someone froze in the house, those numbers are enough to heat it in the worst of all conditions we've know. The far right column is the 140% safety margin over the heating load.
Boilers and furnaces are designed to run continuously. They are not designed for turning on and off 100s of times a day. Boilers are a "little" more forgiving in this regard, but not 400% forgiving. As those demand numbers fall, the system becomes less and less efficient, and has to turn on and off an incredible amount of times, which eats parts. That's bad...
- Maximum Load Matches: Your 125' baseboards can safely emit up to 72,500 BTU/hr on the coldest day of the year. This falls comfortably below the boiler's maximum space heating limit of 150,000 BTU/hr.
This has nothing to do with "Comfortably below". It's TOO BIG. We're aware of what it has capacity to provide, it just can't provide that IN THIS HOUSE. Moreover, it will never be asked to provide that, or anything close to it.
What it really says is no matter what ever happens, there's no way this unit will ever run at anything more than an idle. I only have the numbers for the months you gave me, and I threw in a guess on the Oct days. Those 'warmer' months are where this thing is going to beg for mercy. It is intended to modulate the output so that the burners never turn off. They have the ability to alter the output water temp to match the heating load and they do this with an intelligent controller. Ideally, it will never shut off, and will sense that the water is warm enough to keep the house at a constant temp (not raising and lowering constantly). These have an outdoor sensor that is used along with historical data it stores to tell it how much the home needs to not cycle the unit. Takes a little 'learning' time, but after that it's pretty bulletproof at maintaining a constant temp, which means better comfort.
I already said how this heating and cooling during short cycles is what is killing your inducer fans. It's easy enough to google that I'm not making that up.
- Minimum Modulation Fits: The boiler’s minimum firing rate is 14,000 BTU/hr. Your baseboards only need to be active for about 24 feet (out of your 125 feet total) to safely absorb that minimum heat.
Oct and Nov are below anything that unit can provide. Now what? Ah, yes, even at the 1:10 modulated setting it still can't go low enough. Now, invariably at some point it'll be warm enough that they need to cycle. But that should not be in Dec-Mar...
- No Short-Cycling: Because your total radiation capacity (72,500 BTU/hr) is much higher than the boiler's lowest floor (14,000 BTU/hr), the boiler can easily modulate up and down to match your home's exact heat loss without rapidly turning on and off.
Huh? This guy can't be serious. Short cycling happens when the heating appliance is larger than the heat delivery system (baseboards or ducts) will deliver. This is made worse when the entire system is larger than the house demand. You've got both, in spades. The company makes 2 smaller models, both of which are WAY big enough for your house. What are the reasons for not using one of them?
You've got the house and the baseboards perfect now. The only thing remaining is to size the boiler to match. They're not doing that. This is a recipe for exactly what you have now, a unit that will be dead in no time, or at least a maintenance pain in the ___ .
As to the hot water, I would not do an indirect water heater. That's yet another annoying can of worms. Separate tankless water heater? Yes. Combi? Fine. Indirect? Not so much. I can think of reasons to do one, but in a residential setting, I don't like it.